AC SPD WPX-MPA30-275/3+N
Product introduction:WPX-MPA30-275/3+N surge protective device is for protecting low-voltage consumer’s installations against indirect lightning discharges and is to be installed in LEPM zone: LPZ1 - LPZ2 as per IEC 62312.
Product application:It is suitable for being used in TT, TN-S, and low voltage AC distribution system and provides B class surge protection for three phase power supplies.
Phone number:+86-731-88650578
Contact E-mail:service@hnwpx.com
Specifications
Model Number | MPA30-275/3+N-FM | MPA30-275/3+N |
Art No. | ||
SPD according IEC 61643-1 | Class Ⅱ | Class Ⅱ |
SPD according EN 61643-11 | Type 2 | Type 2 |
Operating Temperature Range | -40℃~+80℃ | -40℃~+80℃ |
Relative Humidity | ≤95%(25℃) | ≤95%(25℃) |
Atmospheric Pressure | 86~106kPa | 86~106kPa |
Working Frequency | 50/60Hz | 50/60Hz |
Rated Working Voltage Uo | 230V AC | 230V AC |
Max Continuous Operating Voltage Uc(L-N) | 275V AC | 275V AC |
Max Continuous Operating Voltage Uc(N-PE) | 260V AC | 260V AC |
Nominal Discharge Current In(8/20μs) (L-N) | 15kA | 15kA |
Max Discharge Current Imax (8/20μs) (L-N) | 30kA | 30kA |
Nominal Discharge Current In(8/20μs) (N-PE) | 20kA | 20kA |
Max Discharge Current Imax(8/20μs) (N-PE) | 40kA | 40kA |
Voltage Protection Level Up(L-N) | ≤1.2kV | ≤1.2kV |
Voltage Protection Level Up(N-PE) | ≤1.5kV | ≤1.5kV |
Response Time tA (L-N) | ≤ 25ns | ≤ 25ns |
Response Time tA(N-PE) | ≤ 100ns | ≤ 100ns |
Response Time for Degradation Indication (320 mA) | ≤ 1min | ≤ 1min |
Max. mains-side Overcurrent Protection | 80A(gL/gG) | 80A(gL/gG) |
Cross sectional area for wiring terminal connected to conductor | Stranded:4~25mm² Solid Wire:4~35mm² | Stranded:4~25mm² Solid Wire: 4~35mm² |
Max. Cross-sectional Area For Remote Signaling Interface | 1.5mm² | |
Intensity of Remote Signalling Alarm Contact | AC:250V/ 0.75A 125V/ 3A DC: 30V/ 2A | |
Insulation between alarm circuit and main circuit | The remote alarm interface is isolated from the main circuit by reinforced insulation on U0 not exceed 230V condition according to EN 60950-1:2006 and with dielectric withstand voltage 3000Vrms. | |
Torque: wiring terminal/remote signaling interface | 2.5Nm/0.25Nm | 2.5Nm |
Enclosure material | PBTV-0 | PBTV-0 |
Degree of protection(IP code) | IP20 | IP20 |
Mounting | DIN35mm rail | DIN35mm rail |
Weight | (525±5)g | (525±5)g |
Diagram of dimensions
Description
AC surge protection WPX-MPA30-275/3+N power module surge protector is consisting of three MOV type power supply module and one GDT, used for L-N, N-PE class two protection.
It is applied to equipotential bonding of the low voltage side of transformer or main low voltage distribution boxes inside the building, providing protection against the overvoltage arising from the lightning strike to power supply system of class I or faulty operation, but they are not applied to the system of the expected short-circuit current beyond rated breaking after flow current.
The series fuse must be at the front-end of the product, otherwise, the surge protector may be burned out by the developed power flow current, while the product is discharging.(option from standard IEC61643-1 and GB50343)